insta wrote:if the power drops while most are running will a 900-1100W unit keep them running?
Each one will draw 170-ish W with the platform heater running, so five together will be 850-ish W. A kilowatt UPS should do the trick, but remember that you want a kilowatt
average, rather than
peak, because the platforms are drawing power for relatively long times and they most assuredly will all go on at the same time.
Also, UPS manufacturers tout VA (volt·amp) rather than W (watt) in the big print, but the power bricks do a good job of power factor correction, so size the UPS based on the small-print wattage number.
putting a pair of deep cycle marine batteries on it rather than the little 7Ah cells they come with.
That won't work the way you expect, because UPS power transistors & heatsinks are sized to handle exactly as much energy as the internal batteries store. If you increase the battery capacity, the power transistors will burn out.
The heatsinks, at least in one UPS in my collection, are actual
sinks: featureless aluminum blocks designed to absorb waste heat
without any cooling airflow. The heatsink (and transistor) temperature rises as the UPS runs, but the battery capacity runs out and the UPS shuts down before the junctions overheat!
Fortunately, the guys who commented on my blog post proposing exactly the same thing smartened me up:
http://softsolder.com/2011/07/22/mge-el ... rangement/
Also, plan to replace the batteries every three years or so; they go bad without warning.
it will wait for me to have every printer going at once
Look on the bright side: the printers will have less trouble keeping the platforms hot after the air conditioning goes out... [grin]
Not that a UPS will give you more than a few tens of minutes more time, but that's more than enough for nearly all power glitches around here.